The disadvantage to that, in addition to difficulty of switching correction as loads change, is that your internal wiring system still has to carry the reactive power as well as the real power.
If your correction is near the load(s), the supply system only needs to carry real power. Your system would benefit the same way the POCO's system does with service-located correction.
Larry, can you help me understand something on this subject? Our POCO has installed PF correction at their transformer. By doing that, they have reduced the reactive power they deliver to us, and also increased the current carrying capacity of their distribution system, correct? If they are not delivering the reactive power to me because of the power factor correction, how is it that I still have reactive power in my distribution system?