Where is the fan motor?
speed 2 and 3 are the same
What closes the uF's?
The normally open contacts. What closes them?
Nope. Look closely at the switch diagram. At medium speed, you have 10uF in series with the run winding. Keep trying.
It should look like this. The high circuit is wired wrong. The red conductor depicts the correct wiring.
![]()
Nope 2 and 3 are the same.
090612-2234 EST
Had I designed the circuit I likely would have used switch position 1 to connect to the node of the three capacitors instead of to the AUX winding.
.
Someone is ignoring the switch pattern in the diagram.
There are four scenarios:
OFF: No voltage to anything
HI: Full voltage to RUN
MED: RUN voltage dropped by current through 10UF
LO: Run voltage dropped by current through 5UF
Bear in mind now that pin 1 of the switch connects to RUN, not to AUX. That is the error.