If a homeowner, who new of electrical work and wanted to install a new oven under the 8 3/4kw limit and the length of the wire under or at the maximum length of 25ft, could that person use a junction box and wire nuts to a new spot using 240.21b2?
OK I will try to answer your question without guessing. :smile:
The conductors running to oven, range or stove top
are not feeders they are branch circuit conductors. (See definitions of feeder and branch circuit in Article 100) The fact that these conductors are not feeders means that none of 240.21(B) applies as those sections apply only to feeders. (See 240.21(B) Feeder Taps)
Also even if 240.21(B)(2) could be used for branch circuits (and it can not be) 240.21(B)(2)(2) requires the tap conductors to terminate in a circuit breaker not utilization equipment.
Now that 240.21(B) is behind us we might be able to use 210.19(A)(3) Exception 1. That exception allows tapping a 50 amp circuit with a minimum of 20 amp conductors that have an ampacity of at least the load to be served. ut it also requires the conductors be as short as possible.
But IMO 210.19(A)(3) Exception 1 is not intended for extending a circuit but it is intended to allow suppling a wall mount oven and counter top stove unit mounted near each other to be served with one 50 amp branch circuit.
HOWEVER, none of the above is on topic, the original poster is asking about a situation where the existing circuit has two hots and Neutral (3 wire stove receptacle) that was also used as the grounding means for the range. He is asking if he can now extend that old 3 wire branch circuit to a new location by using 250.140 exception. The answer to that is no. The new wiring needs to be four wire, two hots, a neutral and a ground. The NEC no longer allows using the neutral as the grounding means for the frames of ranges or clothes dryers.
Now I took the time not to guess and have provided the code references, please take the time to look at the code sections and definitions I listed before responding back. :smile: