lol...guess no one read my post...lol...the debate continued![]()
What post?
Question: What is everyone's view if a range is moved to a location where the existing branch circuit conductors would actually have to be cut shorter rather than extended?Sparky, it is many of our opinions that once a range is moved it is not an existing situation. As Bob pointed out you can ask the ahj to help you on this one but in many areas this would be considered a new installation.
Some inspectors in our area will allow the existing wire if it is not possible, without removal of walls, to add a new circuit.
FWIW: The exception states nothing about its location remaining in place.If you move it you must bring it up to code. I just at a similar situation. Since the existing power source was a 4 wire I was able to add a J box and extend it to the new location. If the conductors had been a 3 wire I would of had to replace the feed from the panel
IMO, the qualifying aspect for the exception is that it be an existing branch circuit for which a grounding conductor does not exist at the outlet or junction box. Sure it does not say the circuit can be extended or shortened, but it doesn't say that it cannot. The mere fact it includes the term junction box seems to imply it can be otherwise routed to some degree.
I say it is not clear and talk to the inspector. :grin:
Do I see a problem with extending the circuit.... Not really as long as the except. conditions are met.
Let's take it a step further and say we change the service and make the original panel a sub panel. Would you still allow, say, the se cable to be used on the existing range-- range is not being touched?
What post?![]()
\Are you saying by putting the old cable in a j-box he could run new wire to the oven and bond the frame?
http://forums.mikeholt.com/showpost.php?p=1064947&postcount=11
I was referring to the guessing remark.....
Keep in mind that I have never done or been on a residential job. Started doing commercial and have been doing it for six years. I have done service entrance cable but only with 350 and 500MCM, cu, all 3ph, hv, lv, transfer switches, generators, and all the little things in between.
I have looked up all the code references that yall have given me. In the first post the postee talks about SE(service entrance) cable as I am to believe. But Iwire has stated that conductors to the oven are a branch circuit. Which to me is a HR.
Why is the postee stating that it is a SE?
And are equipment grounding electrodes not allowed to be tapped or spliced?
And I was just joking as you where.![]()
how was SE used to supply kitchen power?
No is my answer.Let's take it a step further and say we change the service and make the original panel a sub panel. Would you still allow, say, the se cable to be used on the existing range-- range is not being touched?