EMFs from utility transformer

Status
Not open for further replies.

tom baker

First Chief Moderator
Staff member
Question from class today:
For a pad mount transformer, say 25 KVA, 12.5 KV primary, are there any radiated electromagnetic fields if you were sitting on the transformer? (Typical transformer with metal enclosure)
 

techntrek

Member
Location
MD
True for the conductors outside of the enclosure, but the grounded case should act as a faraday cage for the transformer itself.
 

nakulak

Senior Member
Brian is correct. this is the difference between the theoretical faraday enclosure and the practical reality (vents + holes/gaps in enclosure = incomplete shielding)
 

dbuckley

Senior Member
Question from class today:
For a pad mount transformer, say 25 KVA, 12.5 KV primary, are there any radiated electromagnetic fields if you were sitting on the transformer? (Typical transformer with metal enclosure)

Magnetic fields, absolutely. You dont need a guass meter, just pop a CRT monitor nearby.

Back in my working for inverstment banking days we had a chuink of a trading floow we couldn't use 'cos there was a large transformer underneath the trading floor, and it played havoc with the monitors.
 

brian john

Senior Member
Location
Leesburg, VA
Magnetic fields, absolutely. You dont need a guass meter, just pop a CRT monitor nearby.

Back in my working for inverstment banking days we had a chuink of a trading floow we couldn't use 'cos there was a large transformer underneath the trading floor, and it played havoc with the monitors.

Good luck finding CRT monitors in a commercial installation these days.
 