hubertyb00
Member
3, 200 amp panels with seperate meters. I know I run 2/0 to the meters from all of the panels, but what size, or how do I figure out what to run from the meter up the service mast.
I heartily recommend method #1.Two ways to go.
1) Do load calculations and figure out the total combined calculated load.
2) Waste money and run 600 amps worth of conductors.
You're welcome, and welcome to the forum, too! :smile:thanks alot for the advice.
see 230.42Now don't flame me but I always assumed you had to run a wire big enough to carry the max load of the main breaker in the panel??? So what your saying is if I put a 200 amp panel in a house with a caculated load of 125 amps I only have to run 125 amp wire up the riser on the line side of the meter? Umm I'm thinking I'd be back replacing that wire per MY inspector..
Now don't flame me but I always assumed you had to run a wire big enough to carry the max load of the main breaker in the panel??? So what your saying is if I put a 200 amp panel in a house with a caculated load of 125 amps I only have to run 125 amp wire up the riser on the line side of the meter? Umm I'm thinking I'd be back replacing that wire per MY inspector..
Ok yes i understand you can use 310.15b6 but in his case I would assume if your doing 1 service drop on 3-200 amp panels you would have to run either 1250's (which you would never do) or parallel 300's. You would have to make those riser wires rated to the full load....600 amps (give or take a few derate codes)...You coudn't do them at the calculated load of each panel and add them up...There is a possibility that those panels in the future COULD be loaded with more loads so you have to go off of the combined main breakers...or am I thinking wrong here? I've always been taught that your feeder wires have to match your main breaker(s) not just the caculated load...Also in 230.42 that MIVEY was telling me about, it states basically that the wire has to be large enough for the caculated load AND not less than the service disconnect...