Work clearance in front of 13.8kV switchgear
mshields
Boston, MA
For a 13.8kV S&C fuse and switch, switchgear lineup, I'm allowing 5 feet of work space in front of the gear. This I'm basing on the fact that the "nominal voltage to ground" would be 13.8kV/1.73 or 7,976volts. As such, NEC Table 134(A) for condition 2 requires 5 feet of clear distance. I'm being challenged on this and just want to make sure this approach is correct.
Question number 2, the metering compartment has drawout PT's, do I need to allow more than 5 feet in front of it to account for this added depth when the carriage is drawn out?
Thanks,
Mike
Thanks Ron
Thanks Ron
I was pretty sure of myself on this one. But I'm being challened and I wanted to remove all doubt.
As far as your question is concerned, I'll find out. I see where you're going with that and I believe they would be de-energized.
thanks,
Mike
I agree with the approach you used to figure out the working clearance. May I ask what the challenger is saying?
Thanks,
Mike
Wouldn't the 'nominal voltage to ground' be determined by the grounding method used?
I have had utilities require 10' of clearance on a unit sub-station so that they could use hot sticks where the owner was metered at 15kV.
This was a local utility requirement though.
-Ed