For a 13.8kV S&C fuse and switch, switchgear lineup, I'm allowing 5 feet of work space in front of the gear. This I'm basing on the fact that the "nominal voltage to ground" would be 13.8kV/1.73 or 7,976volts. As such, NEC Table 134(A) for condition 2 requires 5 feet of clear distance. I'm being challenged on this and just want to make sure this approach is correct.
Question number 2, the metering compartment has drawout PT's, do I need to allow more than 5 feet in front of it to account for this added depth when the carriage is drawn out?
Thanks,
Mike
Question number 2, the metering compartment has drawout PT's, do I need to allow more than 5 feet in front of it to account for this added depth when the carriage is drawn out?
Thanks,