mtnelectrical
- Essex, New Jersey
Is there any listed wire we could use for undercabinet lights, inside the walls (12 volts)
that's it. There is no other wire we could use?
no,
I remember couples years ago an inspector mention there was a wire that was listed for inside walls, and I am not talking about puck lights that are sold on HD stores
There are certainly CL2 and CL3 low-voltage cables, such as in-wall speaker wire. Is there a readon they couldn't be used?
We use listed wire. I don't know the designation. It's sheathed, stranded pairs..... kind of like fire alarm wire. I will check tomorrow.
411.2 Definition.
Lighting Systems Operating at 30 Volts or Less. A lighting system consisting of an isolating power supply, the low-voltage luminaires, and associated equipment that are all identified for the use. The output circuits of the power supply are rated for not more than 25 amperes and operate at 30 volts (42.4 volts peak) or less under all load conditions.
411.3 Listing Required.
Lighting systems operating at 30 volts or less shall comply with 411.3(A) or 411.3(B).
(A) Listed System. Lighting systems operating at 30 volts or less shall be listed as a complete system. The luminaires, power supply, and luminaire fittings (including the exposed bare conductors) of an exposed bare conductor lighting system shall be listed for the use as part of the same identified lighting system.
(B) Assembly of Listed Parts. A lighting system assembled from the following listed parts shall be permitted:
(1) Low-voltage luminaires
(2) Low-voltage luminaire power supply
(3) Class 2 power supply
(4) Low-voltage luminaire fittings
(5) Cord (secondary circuit) for which the luminaires and power supply are listed for use
(6) Cable, conductors in conduit, or other fixed wiring method for the secondary circuit