They come in Nice patriotic colors as well !!!
It looks great but would get a red tag here.
Where are your bell ends or bushings?
They come in Nice patriotic colors as well !!!
The OP should note that eight 250's don't have the ampacity of four 500's.
Don't you just love the new fall colors? :grin:
It looks great but would get a red tag here.
Where are your bell ends or bushings?
could you please elaborate on this ?
i was going to ask why he would use 250's since he could go down at least a wire size, or did you just state this backwards ?
still at the supply house where they belong...PVC and it is not terminating to the transformer it is stubbed up into it. same as all the PVC in the bottom of the gear in pic 10...I don't recall ever putting bell ends on them like that.
But thanks for the appreciation of craftsmanship...for the "LOOKS" anyways.
Picture on post 10. I've had inspectors say like the yellow wire bent like it is . Is now not the same length
PVC or not the NEC requires it. I can not give you the section right now.
It does look great. :smile:
For what it is worth we come up under transformers like that whenever we can.
8-250's in one conduit would have derating issues which would lower their ampacity.
I think you refering to art.300-4
Yes, it does.I think it looks very good.
could you please elaborate on this ?
i was going to ask why he would use 250's since he could go down at least a wire size, or did you just state this backwards ?
That's what I meant; the OP made it clear he was talking about a single conduit.8-250's in one conduit would have derating issues which would lower their ampacity.
I think you refering to art.300-4
Using 2' radius 90s and the run information in post #8, my pull calc software says the pulling force for the four 500s would be 1065 pounds and for the eight 250s it would be 1088.