12V for Class 2 lighting on Romex?

Status
Not open for further replies.

tls

Member
I have seen Class 2 12V lighting circuits (the low-voltage side) run on Romex or even on BX. Is this really permissible? I can't find any language in section 725 which would seem to allow the use of any cable types other than the CL/CM series for Class 2 wiring outside of conduit.

I keep a spool of 12AWG CL3R around for high-wattage speaker wire and other low-voltage, high-amperage applications, since by the table of substitutions in 725.154 it will work for almost all of them. But this does seem a little silly if I could just use 12/2 Romex. I cannot find any language allowing this, so I think it is not permitted -- am I wrong?
 

kbsparky

Senior Member
Location
Delmarva, USA
Most "NM" cable is rated for up to 600 Volts. 12 Volts is within that operating range, so I see no problem with using it, provided you follow other guidelines for its proper installation.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
I can't find any language in section 725 which would seem to allow the use of any cable types other than the CL/CM series for Class 2 wiring outside of conduit.

Check the hierarchy. A class 1 wiring method trumps everything below it.

-Hal
 

iwire

Moderator
Staff member
Location
Massachusetts
I have seen Class 2 12V lighting circuits (the low-voltage side) run on Romex or even on BX. Is this really permissible? I can't find any language in section 725 .......

How about just using 411.4(A)(1)?

Any Chapter 3 wiring method is acceptable and many times required for 12 volt lighting systems.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
How about just using 411.4(A)(1)?

Any Chapter 3 wiring method is acceptable and many times required for 12 volt lighting systems.


This is true but you must terminate in the approved Chapter 3 fashion. No? unless the system is an approved assembly. That's my take on 411
 

nakulak

Senior Member
i have seen class 2 12v lighting circuits (the low-voltage side) run on romex or even on bx. Is this really permissible? I can't find any language in section 725 which would seem to allow the use of any cable types other than the cl/cm series for class 2 wiring outside of conduit.

I keep a spool of 12awg cl3r around for high-wattage speaker wire and other low-voltage, high-amperage applications, since by the table of substitutions in 725.154 it will work for almost all of them. But this does seem a little silly if i could just use 12/2 romex. I cannot find any language allowing this, so i think it is not permitted -- am i wrong?

725.52 b (2005) (as bob said - insulation needs to be equal or greater than what's in 725.82, then all is well (any chapter 3 method applies)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I use shallow Wiremold boxes with blank plates as J-boxes this purpose.


Odd that the code allows the wire from the puck to be run exposed but the nm cable cannot be spliced to it without a JB. It makes no sense esp. since you can have splices if the cables are exposed from light to light.
 

nakulak

Senior Member
725.52 B says that conductors used for class 2 or 3 must have the insulation rating equal or greater than that required by 725.82. It does not say you have to use an article 300 wiring method per se. In mshio, you can run the nm to the puck. I have, and I will continue to do so until some bonehead inspector acts like a wingnut about it.
 

stickboy1375

Senior Member
Location
Litchfield, CT
725.52 B says that conductors used for class 2 or 3 must have the insulation rating equal or greater than that required by 725.82. It does not say you have to use an article 300 wiring method per se. In mshio, you can run the nm to the puck. I have, and I will continue to do so until some bonehead inspector acts like a wingnut about it.

.
No, but article 411 does. :)
 