no smaller than (per 250.122)How is it sized? Largest OCPD?
sometimesOr is it usually speced out?
What if you're running the IG back to the XO of an transformer. Would it be required to be sized based on the size of the secondary conductors?
What is the proper way to install an iso ground at a sub panel? Do you isolate the grounds in the sub and then drive a ground rod or do you run a seperate ground wire form the sub to the main panel?
Isolated ground circuits are a poor attempt to eradicate stray current; when installed they compromise the integrity of the equipment ground fault path. If circuitry is installed correctly there is no need to separate these equipment grounds (bonds)!
I say the proper way to install isolated ground circuits is not to use them. Think about how the fault current will travel to its supply if the equipment shorts. If required on your drawings question their need.
We think a like, both ski and are in the same profession. We'd get along fine (as long as you learn to say YEP YOU're RIGHT)
But the IG way sells more material good for Kennecott, EC's and workers.
I agree, but wouldn't a transformer-supplied panel technically not be a sub-panel?If your circuit originates in a sub panel supplied by a transformer (separately derived system) the isolated grounds would bond with all other equipment grounds at this particular sub and not at any supply ahead of this subpanel, this is in keeping with 250.118 ?The equipment grounding conductor run with the circuit conductors?.
If your circuit originates in a subpanel not supplied by a transformer the isolated grounds may remain isolated there connecting to a larger isolated EGC to its supply where all will connect.
The number one reason for stray current is incorrect neutral bonding; if this is qualified as correct there really is no need for isolating equipment grounding. Stray or induced current is not trying to return to earth it is trying to return to its source.
Change that to might stop at the sub panel but I make up my bonding n the transformer so the IG will go all the way back to XO at the SDS serving that panel(s).
If you install a TVSS the instructions typically call for the IG of that to go to XO as well.
The IG is not required to be increased in size at the sub panel. Typically IG circuits are all 20 amp so the IEGC could remain 12 AWG.
I agree incorrect neutral bonding is a problem but was not the reasons IGs came to be. If I recall correctly IGs became necessary when the technology and cables connecting data equipment included a ground reference along with the data signals. This would make a loop between equipment.
Modern systems like Ethernet carry no ground references. I believe Gar makes optical solutions for equipment that still use the ground reference.
In my opinion these equipment grounds do not "run with" their circuit conductors causing a violation of 250.118.
Also with longer length than its circuit conductors it may not accommodate VD,
just as if the circuit conductors ran the whole way with would cause 250.122(B) to be applied