3 ph verses 1 ph disconnects
Wgriffin
Virginia
On several different jobs in the past I have used a three phase disconnect as a single phase, and have started getting turned down on device not used as intended. And I actually agree. Here is the thing, I am doing a Univerisity and the engineer is using three phase disconnects as a single phase disconnect and swears it is ok. Who is right???
:smile:
Many of the disconnects I've seen have a diagram inside of the door that depicts single phase connections. Where does is say that a 3 phase disco needs to have a 3 phase supply?
The test requirements for 3-phase switches include 1-phase switching.
Imagine a 3-phase disconnect protected by fuses. If only one fuse blows, the there is no choice but to switch a 1-phase circuit.
Device not used as intended??!!
Please send me in the right direction. The engineer of my job says you can use a 3 phase disconnect on a single phase circuit, but the inspector says that I am not using the device as intended. What and where in the NEC does it say I can use a disconnect in this situation??
Thanks:confused:
I have never seen a three phase disconnect that can not be used on single phase.
You best bet is to find the info from the manufacturer of the disconnects that you are using.
Thanks:confused:
It (the NEC) doesn't.
Sounds like your inspector is grasping at 110.3(B). There is nothing in the NEC that prohibits the use of 2 poles of a 3? disco.
Or what those other guys said.