Generator Conductor Sizing
big john
Portland, ME
Just want some opinions on this: If the feeder breaker is set to the full load capacity of the generator, would that qualify for the 445.13 Exception that allows me to size conductors at 100% of the generator rating?
Seems like "yes," but....
-John
Does the generator have built in circuit breaker? If so and you are asking about the conductors after this circuit breaker 445.13 doesn?t apply.
I could only think there's something in front of the generator that's smarter...
Frankly I can't defer to a dial up breaker on a Gennie, Go look at 450.4, and it states for 125%.
OK, per the Article you should be 115% - otherwise? OK Tag I'm It!
Besides this breaks our chain of thought of a Gen/Motor less than 125%. ;)
So, are you saying it's technically permissable, but maybe just not a good idea? I don't quite follow....
-John
I would say that you must size per 445.13. Which would be 115% of the name plate since you stated that the gen set doesn't have it's own OCP. The only thing I could think of that would allow you to follow the exception would be if the gen. had a over amp shut down built into it.
yeah what ceb said.... if you read the article, it says what it says, what You can do, I never gave it much thought till I read the article, seems I didn't say 115% where is says to use 115%, follow the Code... take it where it leads you... wait I did say 115... I'm going to stop bumming the keyboard