GFCI on 2 wire system

Status
Not open for further replies.

DavidE

New member
Can a GFCI receptacle be installed on a older 2 wire non grounded electrical system?
 
Last edited by a moderator:
Needs more than 10 characters.* :grin:

The plug-in tester has to use the EGC to simulate a shock, because it doesn't have access to the neutral ahead of the current sensor.

If you used a 3-to-2 prong adapter, and grounded the green wire, it would work then.


* If you type extra spaces between the words, the BB system will read them, even though they won't parse.
 