D DavidE New member Jul 24, 2009 #1 Can a GFCI receptacle be installed on a older 2 wire non grounded electrical system? Last edited by a moderator: Jul 28, 2009
I ItsHot Senior Member Location A little piece of heaven! Jul 24, 2009 #3 sticker sticker Don't forget the little sticker.
cowboyjwc Moderator Staff member Location Simi Valley, CA Jul 27, 2009 #4 And do not use your plug in tester to check it.
raider1 Senior Member Staff member Location Logan, Utah Jul 27, 2009 #5 cowboyjwc said: And do not use your plug in tester to check it. Click to expand... You can use a plug checker to check for correct polarity, just don't try to use it to test the GFCI function. Chris
cowboyjwc said: And do not use your plug in tester to check it. Click to expand... You can use a plug checker to check for correct polarity, just don't try to use it to test the GFCI function. Chris
F Flex Senior Member Location poestenkill ny Jul 27, 2009 #6 raider1 said: You can use a plug checker to check for correct polarity, just don't try to use it to test the GFCI function. Chris Click to expand... why not? need 10 characters
raider1 said: You can use a plug checker to check for correct polarity, just don't try to use it to test the GFCI function. Chris Click to expand... why not? need 10 characters
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jul 27, 2009 #7 Flex said: why not? Click to expand... Needs more than 10 characters.* :grin: The plug-in tester has to use the EGC to simulate a shock, because it doesn't have access to the neutral ahead of the current sensor. If you used a 3-to-2 prong adapter, and grounded the green wire, it would work then. * If you type extra spaces between the words, the BB system will read them, even though they won't parse.
Flex said: why not? Click to expand... Needs more than 10 characters.* :grin: The plug-in tester has to use the EGC to simulate a shock, because it doesn't have access to the neutral ahead of the current sensor. If you used a 3-to-2 prong adapter, and grounded the green wire, it would work then. * If you type extra spaces between the words, the BB system will read them, even though they won't parse.
Sierrasparky Senior Member Location USA Occupation Electrician ,contractor Jul 27, 2009 #9 By the way what is a GFIC?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Jul 27, 2009 #10 Sierrasparky said: By the way what is a GFIC? Click to expand... Cut the new guy some slack. :roll: Dave, Welcome to the forum.
Sierrasparky said: By the way what is a GFIC? Click to expand... Cut the new guy some slack. :roll: Dave, Welcome to the forum.
Sierrasparky Senior Member Location USA Occupation Electrician ,contractor Jul 27, 2009 #11 Sorry Was not meant to ridicule
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jul 27, 2009 #12 480sparky said: Click to expand... Well said.