crossman gary
with many elderly and children around it, even if it had only 40 volts potential, I would not want to be the responsible electrician that caused it to happen.
I agree completely and will/would install a proper EGC every time.
the only thing I was trying to say is this sphere of influence is so small, even in the great soil you have, it would not provide a large enough circle of influence to safely bring the earth around the trailer up to a potential that would be safe for everyone that might come into contact with it.
At the very worst, the electrode would do nothing to lessen the severity of the shock. At the very best, the electrode will reduce the potential. Therefore, it seems prudent to install the electrode. Certainly the electrode will not make the shock danger even worse?
you could do the same test I said to Gar, but in this case connect 120 volts to a piece of metal bonded to an 8' rod, with your soil you might have to use a 30 amp circuit, but the effect would be the same, set up to remotely measure the voltages at different intervals from the ground rod, lets say what an average size trailer would be, up to 30' this would give an indication of the voltage a person would come into contact with if they were to touch the trailer from the other side away from the rod.
It might help you understand how small this circle of influence really is.
Precisely the experiment I had in mind. How do you suggest I attach the voltmeter probe to the earth? To me, this could be critical as to the "touch potential" that someone would experience. Maybe a 12" x 12" flat metal plate with a heavy weight on it layed on the ground?
I will probably drive a one foot pipe in the ground for the voltage probe attachment.
But in the two choices in your previous post, knowing either one could kill me, I would chose neither![]()
Not one of the choices!