... and to the grounding electrode(s).
there you go no rod necessary.
well i am seeing it as the electrodes in the originating service location. if i am going to run a egc out to the building. what good does the rod at the secondary location do? it surely wont clear a fault. what i would expect to see is the secondary building bonded to the panel in/at that building. then the egc would carry back to the originating service location to that electrode. with the speed of light at 100 some thousand feet per second how long does it go a couple hundred feet.
only problem i have with it now is, in lightning prone areas, this is asking for trouble.
yeah i get all that but sticking your head in an alligators mouth isnt the greatest idea but yet people keep on doing it. the more buildings you have, the more rods you have, the increased likelihood that the current can go across buildings. for example: lightning strikes the premises system in building C. as luck would have it building A actually provides the least resistance to earth through its electrode. the main service is located in building B. the current could then travel through all the buildings to get to the one that provides the least resistance. there's nothing that says the closest one would be the one that's utilized. so why have so many points of entry, when one defined exit would be more efficient?
Lightning protection is really the only reason (beyond being required to) to have electrodes out at separate structures.
hurk27 said:In most cases, lightning wont even see the GES, as lightning is a high frequency event and most of the time if it even hits a building, it will jump off to the cable system or in many cases the phone system. here we had it jump to a phone line and run about 60' around the outside of a house to then jump to a chain link fence, never even going to the two installed ground rod or the water pipe electrode. so to even say that a small rod electrode will attract a lightning strike is a very loose statement with all the variables that determine what lightning will strike at any point in time. trees can attract many more lightning strikes because they act like a very broad band antenna with many branches of different lengths.
090529-2049 EST
With 120 V applied to the rod I got the following results for earth potential relative to the water pipe and at distances of X ft from the test rod.
3 ft ... 30.5 V
15 ft ... 12.0 V
30 ft ... 6.8 V
60 ft ... 3.5 V
75 ft ... 2.5 V this is about 3 ft from basement wall.
If I were to go to the front side, then the voltage would be the residual voltage from normal ground currents.
.
090531-0825 EST
hurk27:
I believe you misunderstood the point of my experiment.
In an earlier post I stated that a long distributed grounding electrode, such as a conductive water pipe, would be a much better grounding electrode than a vertical ground rod.
Yes, my experiment does demonstrate a large step potential at the vertical ground rod.
But the experiment demonstrates a low step potential relative to the water pipe. At my point 3 ft from the rear of the house I am still 15 to 20 ft from the water pipe, 7 ft down and 8 to 13 ft horizontally. How much conductivity the block wall and cement floor provide is hard to determine. The floor is insulated from the ground by a layer of plastic. Thus, I believe most of the conductivity is thru the earth.
A straight water pipe could be simulated by a number of vertical ground rods and get much the same result if the distance from the string of ground rods to a point source of current injection was maybe 10 times the spacing between the ground rods.
Now consider the farm problem that has been discussed in other threads. If you ringed the barn, and watering and feed area, with a grounding electrode, and all conductive items within this area were bonded to this electrode, then within the ringed area there would be very little difference in potential between different points if the current injection point was outside the ringed area.
090531-0825 EST
A GFCI at the outlet where the trailer was connected in addition to a ground rod at the trailer would probably have been effective.
.
090531-2111 EST Voltage measurements between the trailer body and the earth around the trailer within a step distance probably would be in the few voltage range. The magnitude will be a function of the orientation of the main panel ground rod and the long horizontal rod. Most of the voltage drop between the two rods is at the main panel ground rod. However, if you measured the trailer body relative to the main panel EGC-neutral point it would be about 120 v.
Edited to add that a bolted fault at .2 ohms (supposing an infinite supply) at 120 volts would be about 600 amps, more then enough to clear a 30 amp breakerIf the short is not that low but was at the breaker rating, then it might never blow. Suppose we had 30 A thru 200 ft of #10 copper wire for the EGC, then the drop on the EGC would be 30*0.2 = 6 V. In most cases not too unsafe.