mivey
Finally remembered to ask. According to an actual hands-on person at one of the plants:According to the Southwire rep I talked to, their lengths are -0%, +5%. This does not mean that the measurement is off, only that they may stop the run at a length up to 5% longer than you ordered and you could pay for the extra 5%. That's the official story from Southwire. Well almost, the industrial rep was not in, so they transferred me to the next most official person.
Another manufacturer's rep said they were set up to err on the + side (that's what the plant tells them). Building wire in standard lengths would be paid by the standard length so you would get the extra for "free". For custom-ordered wire, you would pay for the extra that came out of the run. I know some guys at one of their plants and I can get the official scoop from the ones who actually have their hands on the process. I'll ask the next time I'm there, if I don't forget.
Most wire is measured to 0.1" during the manufacturing process. They maintain an average of +/- 1 % when spooling the wire (can actually get to +/- 1/2%). The biggest error is due to human intervention. People stand in a different spot when they cut the wire, spool up the machines differently, re-set the counters differently, are knuckle-heads, just plain out make mistakes, etc.
His advice: If you want X number of ft, you better add the tolerance the supplier gives you or you may be short.