chris kennedy
- Miami Fla.
- Retired electrician
I got a kick out of this. The IT guy has requested 4 of these installs. Note the ground bar is not a 800.100 install, just an equipment bonding jumper.
It might, but we haven't even heard the mission...and decided if we should accept it.:grin:This post will self destruct...........10-9-8-7-6-5-4-3-2............
You may be right, but that seems like an expensive solution.I've got a nickel that says there's two wall warts that are grounded, and cannot go side-by-side if the grounds on both duplexes are the same.
Like a solution for multiple fat wall warts. We have usually recommended power strips. I guess you could also install some wiremold (ugh!).Forget the receptacle install positions, and there is room for further discussion!
In my best Marty Robbins voice:Getting close to hitting the button.:grin:
If you assume the need for two duplexes was just because of the wall-warts...What's so expensive about it? It costs no more to put one duplex in ground up and the other ground down.
That's true. I was just thinking of one receptacle and a power strip. A power strip and/or surge combo usually winds up getting plugged in at a lot of places.Cheaper than 2 single receps, I'll bet.
Many wall warts end up covering both receps of a duplex, and are so thick they cannot go side-by-side unless the duplexes are installed like Chris did them.
Forget about the receptacles, what about the ground bar?
Is there a #6 EGC within the EMT? If not why a #6 to the ground bar?