On several different jobs in the past I have used a three phase disconnect as a single phase, and have started getting turned down on device not used as intended. And I actually agree. Here is the thing, I am doing a Univerisity and the engineer is using three phase disconnects as a single phase disconnect and swears it is ok. Who is right???
:smile:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Many of the disconnects I've seen have a diagram inside of the door that depicts single phase connections. Where does is say that a 3 phase disco needs to have a 3 phase supply?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The test requirements for 3-phase switches include 1-phase switching.

Imagine a 3-phase disconnect protected by fuses. If only one fuse blows, the there is no choice but to switch a 1-phase circuit.
 

Wgriffin

Member
Location
Virginia
Device not used as intended??!!

Device not used as intended??!!

Please send me in the right direction. The engineer of my job says you can use a 3 phase disconnect on a single phase circuit, but the inspector says that I am not using the device as intended. What and where in the NEC does it say I can use a disconnect in this situation??
Thanks:confused:
 

iwire

Moderator
Staff member
Location
Massachusetts
I have never seen a three phase disconnect that can not be used on single phase.

You best bet is to find the info from the manufacturer of the disconnects that you are using.
 

480sparky

Senior Member
Location
Iowegia
Please send me in the right direction. The engineer of my job says you can use a 3 phase disconnect on a single phase circuit, but the inspector says that I am not using the device as intended. What and where in the NEC does it say I can use a disconnect in this situation??
Thanks:confused:


It (the NEC) doesn't.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Sounds like your inspector is grasping at 110.3(B). There is nothing in the NEC that prohibits the use of 2 poles of a 3? disco.

Or what those other guys said.
 