Fire Pump - Grounding
anbm
TX
Designer
Do we ground fire pump ATS? (i.e. run grounding electrode conductor from fire pump ats and bond to building grounding system)? Fire pump can be understood as a separate service, I assumed.
If you are thinking separate service as a (separate building) fed from your main service. Then in 08 it would need a 4 wire any way.
But it might make a difference depending on the type of generator you have.
The Index will list it as a transfer switches, or as a fire pump.
Negating why you have either for a minute.
The Fire pumps need to be addressed as the Big Gorilla in the room, just about all aspects of what you asked is included in 695
Now why you have a fire pump, generator, and transfer switch starts getting addressed in 700.
Well yes you take it to the grounding electrode system of your building its a service .
It is from the power companys transformer and uses the emergency generator via ATS so its a service.