I am working on a crane that is run by a 440 volt 60\hz 1200 kw generator. The company wants a backup generator on the deck ready to wire in. I did the calculations and I belive the amps is 1670 or about 556 amps a leg (by the way this is 3 phase) The electrician above me says we only need 350 mcm the length of the leads will be 120' in thru a barge and up inside the crane in free air with an ambient tempature of 100 degrees F. With the ambient tempature I think I would need at least 500mcm that does not include a voltage drop calculation am I way off and if I'm right should I paralell some wire or just run 500mcm