Grounded & Grounding Conductors Under One Terminal?
ptrombley
Is it a code violation to install a neutral conductor (white) and a grounding conductor (bare or green) under the same screen in a panelboard? This is not a subpanel... this is a typical 120/240V residential service panel. I often see the grounds and neutrals separated, even though the terminal bars are bonded together.
408.41 - Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.
Is this the section you may be looking for? Neutral & grounding conductor can terminate on the same bus in a service, but not the same terminal screw.
You should read read art. 408.41
first.
408.41 Grounded Conductor Terminations.
Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor.
Thanks, Dennis.
I've read that numerous times, but apparently never READ it. My mind-set was "two neutrals were a violation" and I had been allowing a neutral and equipment ground. As the younger folks say "My Bad!"
I wonder why this code is in place. Ground strips are a lot more industrious then din rail terminals and din rail terminals are usually rated for 2 wires.
One of the reasons this code is in place is to relieve one from having to do maintenance and possibly loosen an unintentional grounded conductor while trying to work on the other that is under the same terminal. If one conductor is under the terminal, it becomes more difficult to create that hazard.
first.
That exception mentions nothing about "grounding" (EGC) conductors, just - "Grounded conductors of circuits with parallel conductors" . One would hope the grounding conductors are not part of the circuit - in parallel...
I don't understand your response. The OP asked a question and I believe my posts answered his question. Do you believe it is okay to terminate egc and grounded conductors under the same terminal?
No - I dont think they should be together in the same terminal - maybe I was interpeting your responce to include the exception, to mean you suggest they could?
That makes so much sense now. You would be disconnecting grounded conductors for circuits you are not working on. Thanks
Well, there-- I guess we cleared that one up--- Seems we agree.:grin:
...Do you believe it is okay to terminate egc and grounded conductors under the same terminal?
I'll play devils advocate and say Yes.
(as long as the neutral and ground are for the same circuit)
I see no harm, and an opportunity for a "neater" (more neat?) install...
I'll play devils advocate ...
There can only be one!!!!
That's ahh.... My usual role... ;) And BTW you're wrong...
note to Code Making Panels... add FPN "unless it's neater":)
Wasasparky, I agree with the thought, but Dennis has shown me the light
Once again I have poorly stated my point, let me re-phrase.:roll:
I was not speaking code-wise. I agree code does not allow it.:)
I think the pendulum swung too far with the two neutrals per terminal thing.
I think a neutral & ground in the same terminal is actually a good idea.
(Unless maybe there is a plethora of terminals...)
There, now flame me for the right thing!;):grin::cool:
plethora ??? Flame you ? Heck with words like that I can't even play in your league :)
( I looked it up..very appropriate....and impressive)