I should also say this is from the secondary of a transformer
Still not ok...the conductors must have an ampacity equal to or greater than the rating of the OCPD. 240.4(B) does not apply to these conductors.I am looking at 240.21c . My secondaries might be less the 10 ft long . If they are not is this ok?
(C) Transformer Secondary Conductors. A set of conductors feeding a single load, or each set of conductors feeding separate loads, shall be permitted to be connected to a transformer secondary, without overcurrent protection at the secondary, as specified in 240.21(C)(1) through (C)(6). The provisions of 240.4(B) shall not be permitted for transformer secondary conductors.
Don
Why would 2 sets of 350 kcmil not work for this installation to a 600A overcurrent device?
Only if your raceway for the paralleled conductors is less than 24".If I do a wireway(trough) does that change when I change over to greenfield to enter the transformer?