I should also say this is from the secondary of a transformer
Still not ok...the conductors must have an ampacity equal to or greater than the rating of the OCPD. 240.4(B) does not apply to these conductors.I am looking at 240.21c . My secondaries might be less the 10 ft long . If they are not is this ok?
(C) Transformer Secondary Conductors. A set of conductors feeding a single load, or each set of conductors feeding separate loads, shall be permitted to be connected to a transformer secondary, without overcurrent protection at the secondary, as specified in 240.21(C)(1) through (C)(6). The provisions of 240.4(B) shall not be permitted for transformer secondary conductors.
Still not ok...the conductors must have an ampacity equal to or greater than the rating of the OCPD. 240.4(B) does not apply to these conductors.
Don
Why would 2 sets of 350 kcmil not work for this installation to a 600A overcurrent device?
Only if your raceway for the paralleled conductors is less than 24".If I do a wireway(trough) does that change when I change over to greenfield to enter the transformer?