Pascal must have bored you to death. This is where the learning is. You are an inspiration.
Pascal must have bored you to death. This is where the learning is. You are an inspiration.
Even then, I'd stil, stagger the conductor sizes as the loads diminish with circuit length.A final point: You could just use 240 volt fixtures and you could just use #8 all the way with no neutral.
Yes.Even then, I'd stil, stagger the conductor sizes as the loads diminish with circuit length.
Thank you.mivey
Pascal must have bored you to death. This is where the learning is. You are an inspiration.
I don't think you can necessarily consider single phase loads as "balancing out" the neutral. ..may not be the best idea if you consider that you might lose some of the loads on one phase.
So if I take 1/2 of the % drop from the A or B calc, and add it to 1/2 the % drop from the neutral calc, I would get the total drop.
I find it entertaining as well. It keeps the old cobwebs cleaned out.
I bet if one metered the neutral the data would support this to be a safe installation.I don't think you can necessarily consider single phase loads as "balancing out" the neutral. Otherwise we could say we will balance our panels and use a very small neutral.
A final point: You could just use 240 volt fixtures and you could just use #8 all the way with no neutral.
The formula you reference is indeed in the Red Book but is the approximate formula. The Red book also has the exact formula, which is the one I use.There is an IEEE Red Book Std 141 formula for AC V-drop, illustrated after Table 9, in the 2005 NFPA 70 handbook. The last word on any formula tweaks may be found with member kingbp's "Validated & Verified" model called ETAP load flow. This apparently uses physical wires and loads for calibration.
Sorry to be so blunt, but your premise is flawed. It is impossible to have 3.6V drop at light #1 and also at light #10, with one exception, and that is if you use separate wires from the source to each load.As I see it, you need to do a reverse calculation to allow for all loads and end up with appropriate voltage drop. To do this, start with the fartherst light and assume maximum amperage and work your way down.
At 2.5 A per lamp each side of the line would carry half the load, or 12.5A
1. 3.6V /12.5A =.288 max. ohms/1.6=max of .18ohms per m = #1wire to second light @ 320' (Odd numbers are listed after even numbers because last light has an even number)
2. 3.6V /12.5A =.288 max. ohms/1.44= max of .18ohms per m = #2wire to first light @ 160'
3. 3.6V /10A =.36 max. ohms /1.28=max of .28ohms per m = #3wire to fourth light @640'
4. 3.6V /10A =.36 max. ohms /1.12=max of .32 ohms per m = #3wire to third light @480'
5. 3.6V /7.5A =.48 max. ohms /.96=max of .6 ohms per m = #6wire to sixth light @960'
6. 3.6V /7.5A =.48 max. ohms /.8=max of .5 ohms per m = #6wire to fifth light @800'
7. 3.6V /5A =.72 max. ohms /.64=max of 1.12 ohms per m = #10wire to eighth light @1280'
8. 3.6V /5A =.72 max. ohms /.48=max of 1.5 ohms per m = #10wire to seventh light @1120'
9. 3.6V /2.5A =1.4 max. ohms /.32=max of 4.4 ohms per m = #14wire to tenth light @1660'
10. 3.6V /2.5A =1.4 max. ohms /.16=max of 8.75 ohms per m = #14wire to nineth light @ 1440'
If you follow this scenario to the extreme, you will end up with a single 120v circuit, with half of the power at half of the voltage, having the same current, resulting in the same voltage drop, so there's no increase in overall voltage drop.Also, in the event of one fixture becoming disfunctional in the sense of non-conductive, the neutral conductor picks up the imbalance and voltage drop to the other working fixtures remains within nominal voltage tolerance. Of course that will change as the number of non-conductive fixtures powered by one leg increases.
Afraid not.If you follow this scenario to the extreme, you will end up with a single 120v circuit, with half of the power at half of the voltage, having the same current, resulting in the same voltage drop, so there's no increase in overall voltage drop.
This is roughly true as explained above, and only while all "banks" are on. Turn all but one off and and the one remaining on is no different than an individual branch circuit. To utilize the lesser voltage drop of a MWBC, it should be ascertained within reason that all banks will be on or off simultaneously.This is one of the reasons we pro-MWBC guys like them; there's potentially half as much system-wide voltage drop as there would be with individual circuits; same with 3ph. It also points out why shared neutrals need not be counted as CCC's.
They do have a knack for finding the worst case scenario.I am of the opinion if one "bank" or major portion thereof is not working and not restored to working condition within a reasonable amount of time, the owner of the lighting array deserves the consequences.
That's unfortunate. In addition to including adjustable parameters (like temperature), I think most should model a constant VA (like heavy industrial motors), constant impedance (typical for most commercial and residential loads), or constant current (essentially the same as 1/2 & 1/2 of the VA & impedance models). Some more sophisticated models use voltage & current measurements to define exponential load models or quadratic equations for the real & reactive power.lower voltage equates to lower current... something I see very few stepped VD drop calculations take into account.
Good answer.Afraid not...FWIW, the following depicts my basic 3% VD calculation for the OP's case using Excel...
lower voltage equates to lower current...
Ooops. I think we overlooked the fact that in the OP there was mention of ballasts being used, not incandescent.Good answer.
Righto ye ar daer mateyOoops. I think we overlooked the fact that in the OP there was mention of ballasts being used, not incandescent.
I agree... and what of more traditional magnetic ballasts?If these are more like the universal electronic ballasts, these should be modeled more as constant VA loads instead of constant impedance loads, i.e., lower voltage equates to higher current.
For those, and even some electronic ballasts, the current drops with voltage.Righto ye ar daer matey
I agree... and what of more traditional magnetic ballasts?