Emergency lighting in patient care area

Status
Not open for further replies.

shaw0486

Senior Member
Location
baltimore
I had an electrical inspection today on a project and the electrical inspector adviced me that i would need an em light in the exam rooms does anyone knw what code requirement this is. NEC, NFPA, IBC, ect.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I don't think the NEC has a rule about lights in patient care areas. Receptacles, yes, but not lights. Ask the inspector for a code reference.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
What type of facility is this?

Are the exam rooms non-hazardous anesthetizing locations?

Chris

This would play a factor in whether a battery pack type fixture is required.

Roger
 

raider1

Senior Member
Staff member
Location
Logan, Utah
This would play a factor in whether a battery pack type fixture is required.

Roger

I agree, the OPer said the inspector was asking for an emergency light in the exam rooms.

517.63(A) requires a battery powered emergency lighting unit installed in non-hazardous anesthetizing locations. These battery units need to installed in accordance with 700.12(F) which deals with emergency unit equipment.

Dentist's exam rooms with nitrous oxide would need to comply with this section.

Chris
 