mkgrady
- Massachusetts
I wired a couple of boilers today in a small manufacturing facility. They are insisting that a ground rod be installed through the slab at each boiler control panel. I asked them why they wanted the rods and they indicated they had problems in the past where fault currents burned up some of their equipment.
The building has a 120/208 system. All circuits are in emt or GRC (the older stuff). My contact explained to me that they don't have the green wire in their circuits so they install rods at all equipment. I explained that the conduit is the grounding conductor. I couldn't convince him that all their ground rods were unnecessary. He said two electricians told him it's a good idea.
They are driving the rods and are running #6 CU, thhn from the rods to the equipment. They asked me where they should connect the #6 at the boiler control panel. The BCP only requires a 15 amp 120 volt circuit so it's not like the #6 will fit in the tiny little connection box. I told them if they insist on connecting the BCP to a rod they can just drill a hole in the cabinet and install a lug on the outside.
My questions are: What good is the rod if the emt feeding the equipment is in tact? Are there any detriments to adding a ground rod at equipment? Does it violate the code in any way?
Thanks, Mike
Thanks, Mike