- Windsor, CO NEC: 2023
- Hospital Master Electrician
Anybody see any problems with this one-line?
Yeah, I figured, why bother. There's two panels in the house.As long as your load is less then 200. It looks good to me.
I think you can use 2/0 cu on an SFD,
The inverter kills the upstream if it detects a loss. Hence the two panels in the house.I don't see anything to prevent backfeeding the utility due to a power-outage, but the one-line for the pv equipment isn't shown unless I missed something.
That's the solar guy's problem. I bet the inverter does it itself.Forgot to add that I didn't see anything that syncs the pv to the grid either.
What more would you add? I am doing just the work shown, minus Panel PDP which is installed by the solar guy. I am pulling the 60A feeders. Anything actually PV will have to be drawn on the solar detail by the solar guy.What is shown looks OK but there is a lot missing.
You just said a mouthful.Your past the hurdle of bus capacity and two feeders.
You just said a mouthful.![]()
One more thought. What are your thoughts on feeding one building with two feeders, knowing that one comes from the inverter and one from the utility?
Yeah, there's batteries. And a generator ties into the inverters too. I think there's a few donkeys on treadmills in the wings, too.![]()
External Disconnect Switch: For Listed inverters, the Company may require an external disconnect switch (or comparable device by mutual agreement of the Parties) at the PCC with the Company or at another mutually agreeable point that is accessible to Company personnel at all times and that can be opened for isolation if the switch is required. The switch shall be gang operated, have a visible break when open, be rated to interrupt the maximum generator output and be capable of being locked open, tagged and grounded on the Company side by Company personnel. The visible break requirement can be met by opening the enclosure to observe the contact separation. The Company shall have the right to open this disconnect switch in accordance with this Interconnection Tariff.