Only if we want to line to say "no" one by one. :grin:Simple answer, no go. For some reason I feel ten pages coming...![]()
Only if we want to line to say "no" one by one. :grin:
:grin:....................................................
Thanks Guys, I guess I'm just having trouble getting the difference between a small appliance outlet and any other piece of utilization equipment outlet.
Thanks Guys, I guess I'm just having trouble getting the difference between a small appliance outlet and any other piece of utilization equipment outlet.
Small appliances like toasters, blenders, elec skillets, etc are not fixed in place. A food waste grinder would be fixed in place.
Simple answer, no go. For some reason I feel ten pages coming...![]()
Sorry Guys, still not getting it. Where does it mention or exclude appliances that are fixed or held in place ?
It doesn't do either, in that it doesn't talk about any actual appliances. The "small appliance circuit" might be badly named, but the general notion (as has been mentioned) is to make sure the owner has places to plug in the coffee pot, and the toaster, and the food warmer on the dining room table, and other such things. The actual requirement is that certain specific receptacles get their power from SA circuits, and that nothing else gets its power from the SA circuits.Sorry Guys, still not getting it. Where does it mention or exclude appliances that are fixed or held in place ?
Speaking of the disposal only. Now that it is a cord appliance I can find no reason to turn you down.
But wait I will be challenged on this.
I'll go 1st on the challenge. 210.52b1 states that " the 2 or more samll appliance circuits required by 210.11c1 shall serve all wall and floor receptacles covered by 210.52a, all countertop outlets covered by 210.52c, and receptacle outlets for refrigeration equipment."
The waste disposal (even cord and plug connected to a wall receptacle in the cabinet) is not covered in 210.11c1, 21052a, or 21052c so may not be connected to the SABC's.
I agree with Jim on this one. The disposal can be plugged into a receptacle outlet, but that outlet cannot be powered by an SA circuit.