dennislewis2001
can you put a 90 mc connector into the side of a 4 gang box?:-? and if not why not:-?
There is no 300.15d.. There is a 300.15(D) which is for MI cable. Are you installing MI cable?
Yes, you can. What does the 300.15 2008 code say? Here in CA, we still go by the 2005.
~Matt
300.15 (F) Fitting. A fitting identified for the use shall be permitted in lieu of a box or conduit body where conductors are not spliced or terminated within the fitting. The fitting shall be accessible after installation.
So what is the problem with a MC 90 degree fitting into a box? You are using the correct fitting, aren't you?
yes i am using the right fitting...is there anywhere alse in the 2008 code book that says different?
The 90? MC connector is not being used as a box - it connects the MC to the box. Look at the title to 300.15, it covers boxes.As I read 300.15(F), if the fitting is not accessible, then it is a violation.
Can you provide more details of the installation in question?