JFletcher
Senior Member
- Location
- Williamsburg, VA
The 90? MC connector is not being used as a box - it connects the MC to the box. Look at the title to 300.15, it covers boxes.
Ah, I see now. Thanks George.
The 90? MC connector is not being used as a box - it connects the MC to the box. Look at the title to 300.15, it covers boxes.
300.15 Boxes, Conduit Bodies, or Fittings ? Where Required.
Total guess here, but maybe the inspector is confusing the requirements for FMC with the requirements for MC.
348.42 prohibits the use of concealed 90 degree connectors with FMC.
There is no such prohibition with MC.
Mike IMO a connector is just a specific type of fitting.
Those are definitely not permitted inside angle connectors.Yes you are right. For some reason or the other my mind went to one of these
![]()
I suppose it must have been the time of morning that caused this laspe in mental ability :grin: as though I don't jump off the deep end once in a while.
MC cable - not a re-pullable flex run? Not splicing or terminating? OK then....300.15 (F) Fitting. A fitting identified for the use shall be permitted in lieu of a box or conduit body where conductors are not spliced or terminated within the fitting. The fitting shall be accessible after installation.
So what is the problem with a MC 90 degree fitting into a box? You are using the correct fitting, aren't you?
I would imagine just about everything is concrete tight when tapped.Look closely - "Concrete tight when tapped" - Conceal it? - You can even pour it...
I agree... yet 300.15's general requirement seems to differentiate them: "Fittings and connectors shall be used only with the specificMike IMO a connector is just a specific type of fitting.
Fitting in this context is one used in lieu of a box or conduit body.I think the use of the word "Fitting" in this section is wrong, as it doesn't line up with the definition in 100,
to me 300.15(F) is describing a condulet body or something big enough that would permit a possible splice, other wise the wording just doesn't make sense, a 90? fitting would never have enough room to ever think of making a splice in it?
And if was put in here for FMC, 348.42 (2002) already covers this.