mcelweec@gmail.com
CMAC1
- Location
- NYC
- Occupation
- Electrician
who is responsible for enforcing the installation of panic hardware,the EI or the building department?.
Are we talking about panic bars on an electrical room door? Then the answer is yes, either one might call it. If you are talking about panic bars for exiting, it will usually be the buiding inspector or fire inspector.
Now just as most guys think that combo inspectors don't know anything about electrical, don't assume that the electrical inspector doesn't know anything about building codes.
Are we talking about panic bars on an electrical room door? Then the answer is yes, either one might call it.
110.26(C)(3) Personnel Doors.
Where equipment rated 1200 A or more that contains overcurrent devices, switching devices, or control devices is installed and there is a personnel door(s) intended for entrance to and egress from the working space less than 7.6 m (25 ft) from the nearest edge of the working space, the door(s) shall open in the direction of egress and be equipped with panic bars, pressure plates, or other devices that are normally latched but open under simple pressure.
Since the OP posted this in the NEC section, I was assuming we were talking about electric rooms.This is a NEC issue.
I didn't. Aside from an electrical room they would have no authority on crash bars, is what I should have said. The EI cant demand crash bars on the front doors, but he certainly can point it out to the owner, GC, EC, Fire Dept and Building Dept.
I would as a rule agree with you, but many a time I will tell a contractor that he is going to need to do something and he can either wait until the inspector tells him to or do it before he's required to, though I would never write a correction notice on it.