5-254 Log #3527 NEC-P05  Final Action: Accept in Principle in Part 
(250.104(C)) 
_______________________________________________________________ 
Submitter: Phil Simmons, Olympia, WA 
Recommendation: Revise the existing text of the 2008 NEC as follows: 
(C) Structural Metal. Exposed structural metal that is interconnected to form 
a metal building frame and is not intentionally grounded or bonded and is 
likely to become energized shall be bonded to the service equipment enclosure, 
the grounded conductor at the service, the grounding electrode conductor if 
where of sufficient size, or the one or more grounding electrodes used. The 
bonding jumper(s) shall be sized in accordance with Table 250.66 except as 
permitted in 250.104(A)(2) and (A)(3) and installed in accordance with 
250.64(A), (B), and (E). The points of attachment of the bonding jumper(s) 
shall be accessible unless installed in compliance with 250.68 Exception No. 2. 
Substantiation: The phrase ?likely to become energized? is proposed for 
deletion as most often, electrical inspectors enforce bonding of structural metal 
if the building or structure has exposed metal members and the building or 
structure is supplied with a service, feeder or branch circuit.  
   The reference to 250.104(A)(2) and (A)(3) will allow adjustment in the size 
of bonding conductors and jumpers if the building s supplied by a feeder.  
   The reference to 250.68 Exception No. 2 permits the connection of bonding 
conductors or jumpers to be fireproofed and not be accessible if appropriate.  
   Section 3.3.4 of the NEC Style Manual states that ?where? should not be used 
to mean ?when? or ?if.? This proposal intends to use the word ?if? where 
appropriate. 
Panel Meeting Action: Accept in Principle in Part 
   Revise text to read as follows: 
(C) Structural Metal. Exposed structural metal that is interconnected to form 
a metal building frame and is not intentionally grounded or bonded and is 
likely to become energized shall be bonded to the service equipment enclosure, 
the grounded conductor at the service, the disconnecting means for buildings or 
structures supplied by a feeder or branch circuit, the grounding electrode 
conductor where if of sufficient size, or the one or more grounding electrodes 
used. 
The bonding jumper(s) shall be sized in accordance with Table 250.66 
and installed in accordance with 250.64(A), (B), and (E). The points of 
attachment of the bonding jumper(s) shall be accessible unless installed in 
compliance with 250.68(A) Exception No. 2.
 
Panel Statement: 
The panel does not accept the deletion of ?likely to become energized?. If the AHJ believes the structural metal is likely to become 
energized then bonding is required. There is no reason to eliminate the 
flexibility provided when situations occur involving structural metal that is 
unlikely to become energized. The panel does not accept the recommendation 
to refer to Sections 250.104(A)(2) and (A)(3) because these sections cover 
bonding of metal water piping. The panel action on Proposal 5-253 has been 
incorporated into the panel action on this proposal. 
Number Eligible to Vote: 16 
Ballot Results: Affirmative: 16