I have an existing MCC lineup that was put in 1983. When they ran the main power to this group they did not run a neutral from the power source. My question is can I run a neutral in a separate conduit from the power source to give me a neutral in the existing MCC?
I would guess the op wants to run some 277V loads.Why do you need it? ...
cf
That's true, that's what he said - Which does not change my guess.He said MCC. Not load center
I wanted to feed a 480/277 NF panelboard from a bucket in the MCC.
cf
Well, you need to feed the panelboard from a slash rated panel. Not that MCC
He could feed it from the MCC if the MCC had a neutal.
He can still do it from the MCC with the addtion of a 480 x 480Y/277 transformer.