T TDevries Member Nov 5, 2009 #1 Is it okay to feed a 1 phase 10kva transformer with a 3 pole 480vac breaker. I have had some varied responses from the local jurisdiction on this. I do not see anything in the code that says specifically I can not do this, any ideas?
Is it okay to feed a 1 phase 10kva transformer with a 3 pole 480vac breaker. I have had some varied responses from the local jurisdiction on this. I do not see anything in the code that says specifically I can not do this, any ideas?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Nov 5, 2009 #2 You may do so.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Nov 5, 2009 #3 augie47 said: You may do so. Click to expand... He's so nice! :grin:
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Nov 5, 2009 #4 LarryFine said: He's so nice! :grin: Click to expand... That didn't come out right, did it It would not be a violation of the Code to do that, as far as I know. (better ?) Last edited: Nov 5, 2009