Yeah, Ken. But somewhere I thought I read or misread that when replacing an outlet, if in an area that now requires GFI, a GFI recep or protection is required. As I said earlier, I don't have my code book. If I'm wrong, I gaurantee it's not the 1st. time.210.8 is the GFCI requirement. 406 only requires the recep be grounded.
Yes, now the question, if you pull a new homerun, can you put the new recep on the same ckt as the new h/v/l, if the ckt does not leave the bathroom?.
By the way this paticular job required the addition of a recept outlet on the other side of the sink. Of course that would require a new 20 amp would't it?
Yeah, Ken. But somewhere I thought I read or misread that when replacing an outlet, if in an area that now requires GFI, a GFI recep or protection is required. As I said earlier, I don't have my code book. If I'm wrong, I gaurantee it's not the 1st. time.![]()
I left for a while, pop some bubble wrap, have lunch w/ my mom, & grab my code book.but why would you !
look at 210.23(a) (1) It clearly says you cannot. The HVL is a piece of utilization equipment as defined by the NEC. The HVL was not an original installed unit.
Now the weird thing is how practicle would it be to leave the one recept alone and the new one GFCI'd
I have seen exactly that.
Remember all the drywall was removed.
Yes, i know 210.8 covers GFI.406 doesn't deal with required GFCI protection for kitchens & baths, that's back in 210.8.
406, when replacing receptacles, either requires they be grounded, or replaced with a 2-slot, or be GFCI-protected with a label.
Help me out w/ this please. 406.3(D) Replacements. (D)(2) GFCI: GFCI protected outletsshall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this code.
Does that mean if there is an unprotected recep in an older kitchen, bathroom, wherever, & you replace the recep, does it have to be repalced w/ a GFCI protected recep.?
I say so, also. ThanksI'd say so
Sorry, I have to disagree.No, I'd say 210.8 says to replace it with GFI protection.
406.3(D) is for replacing receptacles where there's no grounding conductor.
210.8 GFCI Protection
406.3(D)(1) Grounding type receps.
(D)(2) GFCI
(D)(3) Non-grounding type receps.
The way I read it, right or wrong, 210.8 tells us where required.
406.3(D) is for replacement receps. grounded or not.
Whew! Thanks, now I don't have to pop more bubble wrap. :grin:I gotcha. I'm just thinking of replacing receps where there's no ground. Even if there is, 406.3(D)(2) requires a Giffy if the location requires it.
I wouldn't put the recep & HVL on the same ckt - just asking.
Practical or not, I beleive code will allow it.
As all the drywall is removed, & the HO is willing to pay for any & all upgrades, no problem.