ivsenroute
- Florida
To the other inspectors:
Is it just me or are there any other areas where electricians are somehow convinced that NM and UF cable is actually THHN and allowable ampacity is out of the 75 degree column?
I should not have to spend any more time trying to educate both electricians and supply houses that a 50A Range or a 50A Hot Tub needs to be supplied by 6/3 NM cable and not 8/3. If they want to use 8awg copper then run conduit and pull THHN. This has been happening all year long.
334.80 Ampacity.
The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The ampacity shall be in accordance with the 60?C (140?F) conductor temperature rating. The 90?C (194?F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60?C (140?F) rated conductor. The ampacity of Types NM, NMC, and NMS cable installed in cable tray shall be determined in accordance with 392.11.