Okay so in 250.122(B) it states" Where ungrounded conductors are increased in size, equipment grounding conductors, where installed, shall be increased in size proportionately according to the circular mil area of the ungrounded conductors".
So the argument that some of my co-workers and I had was this. They felt that the rule only applies when you intentionally upsize the ungrounded conductors. For example: voltage drop, or engineer spec. But I felt that it would apply no matter what. For example: you need to pull a 20 Amp circuit, it calls for # 12 Awg . And all you have left is #10 Awg. But you still had enough #12 to pull for the egc. (this was the actual setup that was being pulled in for most of the branch circuits). I feel like you would need to pull a #10 egc with #10 ungrounded conductors, even though it's a 20 A circuit. what do y'all think?