Multiple voltages
Yes you can. You'll have this scenario anytime you run a Multi-Wire Branch Circuit.
Roger
210.4 for one.
BTW, welcome to the forum.
Roger
You also can have circuits from different panels or different services for that matter within the same conduit.
Can you have multiple voltages such as single phase 208 and 120 in the same conduit that come from the same panel
Sure u can. keep in mind the derating factor starting from 4 current car. conductors:
4?6 80
7?9 70
10?20 50
21?30 45
31?40 40
41 and above 35 (percent) :)
What about 300.3(C)(1) 600 Volts, Normal, or Less.
Says as long as the insulation is rated to the highest voltage you can mix any voltage under 600 volts, AC or DC
But in NYC voltages over 250v can not . 300.3(C)(1) Ex. No. 2
Art 725 shoots a hole in assuming any mix is allowable if the insulation rating is high enough.
Care to explain what this NYC amendment to the NEC means?
[FONT=TimesNewRoman,BoldItalic][FONT=TimesNewRoman,BoldItalic]ARTICLE 300[/FONT]
[FONT=TimesNewRoman,BoldItalic]Wiring Methods[/FONT]
[FONT=TimesNewRoman,BoldItalic]SECTION 300.3[/FONT]
[/FONT]
[FONT=TimesNewRoman,Italic][FONT=TimesNewRoman,Italic]Subsection 300.3(C)(1) - Add a new Exception No. 2 to read as follows:[/FONT][/FONT]
[FONT=TimesNewRoman,Italic][FONT=TimesNewRoman,Italic]Exception No. 2: Barriers shall be provided to isolate conductors energized from[/FONT][/FONT][FONT=TimesNewRoman,Italic]
[FONT=TimesNewRoman,Italic]different sources when system voltage exceeds 250 volts nominal and conductors are[/FONT]
[FONT=TimesNewRoman,Italic]protected by first or second level overcurrent protective devices. Sources include service [FONT=TimesNewRoman,Italic]
[FONT=TimesNewRoman,Italic]entrance points, secondaries of different transformers, generators and UPS systems.[/FONT]
[/FONT][/FONT]
[/FONT]
I don't think we judge which one can beat up the other one :)
You have to follow the applicable Article. Art 300 in General Wiring Practice. Special conditions, such as Art 700, take precedence when applicable. Same as Pool Wiring sets forth specific rules.