Was reading about unbalanced neutral on previous posts and came across this quote from Augie
(The exception is where, on a three phase system, the major portion of the load is non-linear (electronics, ballasts, etc) you must still count the neutral.
On a normal run with 20 amp circuits and #12 THHN you have to exceed 9 ccc to create a problem, so a good rule of thumb is just keep your conduit fill to 9 wires (+ equip ground) and avoid the problem.)
Question #1 doesnt Table 310.15(B)(2)(a) Adjustment Factors for More Than Three Current-Carrying Conductors in a Raceway or Cable necessary when using 9 conductors?
Question #2 so if one neutral and three hots are used on ballast lighting from 3 different phases of a 277v system the neutral carries current?
Thanks for any clarity on this
(The exception is where, on a three phase system, the major portion of the load is non-linear (electronics, ballasts, etc) you must still count the neutral.
On a normal run with 20 amp circuits and #12 THHN you have to exceed 9 ccc to create a problem, so a good rule of thumb is just keep your conduit fill to 9 wires (+ equip ground) and avoid the problem.)
Question #1 doesnt Table 310.15(B)(2)(a) Adjustment Factors for More Than Three Current-Carrying Conductors in a Raceway or Cable necessary when using 9 conductors?
Question #2 so if one neutral and three hots are used on ballast lighting from 3 different phases of a 277v system the neutral carries current?
Thanks for any clarity on this