"250.24(A)(4) Main Bonding Jumper as Wire or Busbar.
Where the main bonding jumper specified in 250.28 is a wire or busbar and is installed from the grounded conductor terminal bar or bus to the equipment grounding terminal bar or bus in the service equipment, the grounding electrode conductor shall be permitted to be connected to the equipment grounding terminal, bar, or bus to which the main bonding jumper is connected."
I would agree with you, but after reading Oakey's question about the GEC from the water pipe wouldn't you follow 250.24(A)1? Which, the way I read it, say that the GEC must be terminated where the grounded conductor is terminated.
Isn't the main bonding jumper the wire that connects the the two together? In most cases the green screw or bus connection the panel to the grounded bar.