what are you measuring ? (Load side of switch to neutral, Load to ground, etc)
and what type meter are you using ?
 

walkerj

Senior Member
Location
Baton Rouge
If you are using a digital meter load to neutral and there is a downstream load on the neutral I think you could measure a voltage :-?
 

SG-1

Senior Member
Fluke offers this as a solution. I bought one from a local supplier. $40-$45
It places a 3000 ohm resistor across your leads to bleed off the phantom voltage. It is CAT IV 600V rated.

Fluke SV225

Meter manufactures are offering Low Z settings built into the digital meters now to address this issue.

Disclaimer: This may not fit your particular brand of meter.
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
Something sounds wrong here. If there is a working load such as a light bulb on this load side of switch it should kill any stray voltages. That is assuming with switch on the load works.
 

pfalcon

Senior Member
Location
Indiana
Also backfeed from another circuit. I had this in my rental property where the tenant did some creative wiring. The EL had to separate the circuits and remove the dual fed components.
 