quinn77
Senior Member
- Location
- Lake Jackson, TX USA
I recently installed a vfd system for a new wastewater project in Tiki Island, Texas where the engineer had spec'd individual THHN conductors for 4 7.5 hp drive motors in one 2" pvc conduit. The engineer's design also had the last motor about 220' from the vfd. After approx. 90 days, the conductors had started to fail. The water table there sits at 18", and the labor that I had been provided failed to follow specs given for fitting the conduit, so; in replacing the feeders I had found the conduit to be full of water and what looked like "nicks" and holes blown in the insulation of the conductors. After doing research on vfd installation, I'm starting to think the engineer has made multiple mistakes on the design of this system. He also seems to think that filters and other electrical components will resolve this problem. I'm feeling the responsibility on this one and would like an engineer's feedback on this.