800 amp ATS
Controls Guy
Central PA
I am writing to request a common sense test on specifying a new ASCO 4000 automatic transfer switch for a waste treatment plant.
This is a an underground replacement service with new 800A 480 3 phase disconnect and tentatively an ASCO model 4000 service entrance rated transfer switch.
1) Does anybody have good/bad experiences with the ASCO 4000?
2) Should I select a switched neutral or a solid neutral connection in specifying the model? Common sense indicates a switched neutral would be more advantageous, in case there is issues with the utility.
Thanks
chris kennedy
Miami Fla.
60 yr old tool twisting electrician
Wrong forum for that.
They are on par with Kohler and Lakeshore. Have you priced Russelectric? They are top of the line IMO.
Under 1000A and a 480y/277, IMO a 3 pole is fine, but I'm just an installer.
Welcome to the Forum.
dbuckley
Whenver possible I'd always suggest a solid neutral so (a) the neutral is less likley to fail open with all the cost and pain a lost neutral incurs, and (b) to reduce the impedence on the neutral leg.
Sometimes you are required to switch the neutral, but if you dont have to, its one less thing to go wrong.
yired29
Thanks
Keep in mind if you go with a switched grounded conductor then that constitutes a separately derived system and the rules of 250.30 apply.
Controls Guy
Central PA
Thank You for Feedback
Feedback and value-added comments are very much appreciated. Looks like half a dozen one way and six another. I will certainly check into the Russel ATS.
Merry Christmas - The Controls Guy
jrannis
Thanks
IMHO, ASCO is overpriced for what they are
Unless its all busbar,
Please set it up so that the utility, generator and load are in the correct location for the feeders to enter without having to cross each other
Solid neutral for sure!! Unless you are designing a separately derived system
dduffee260
Texas
We just supplied a Cutler Hamer 800 amp ATS. It was around $6300 if I remember correctly. The ASCO was going to be $9500. There is no way the ASCO was worth that much more. Besides ASCO was almost impossible to contact and deal with.
infinity
New Jersey
Journeyman Electrician
ASCO is a local company so I'm not sure we've ever used a different product. I agree completely that they're overpriced.
Controls Guy
Central PA
ASCO Prices
ASCO Prices
Thanks to everyone that commented on my post!
As for pricing, I obtained two comparisons for a service entrance rated, NEMA 12 and 4 pole.
ASCO came in at about $14,000 and Eaton was well north of $15,000.