I say no but predict this will be a long thread. :grin:
I agree with Bob however I don't think there is any article that will support this either. I think of it as common sense.![]()
for purposes of box fill I agree but why as far as derating ccc in a conduit due to heatThere are no exceptions for common sense:grin: They must be counted as two CCC's
If you have two loads installed in a raceway that will not operate at the same time do you need to count all of the conductors as CCC, I never do.
One possible situation would be heating and cooling circuits installed in same raceway or maybe a normal process load vs a cleanup load where the two loads would never run simultaneously.
I just registered a year ago. I can't believe this question hasn't been asked before?would you have to count travelers of a 3way switch as two current carrying conductors since only one would carry current at a time.![]()
Agree and agree.I say no but predict this will be a long thread. :grin:
Hard to argue with this statement A similar situation exists for feeder and service calculations as well as neutrals carrying unbalanced current.I can't find one that permits it, but also can't find one that prohibits this either. Am suggesting that it is a similar situation to the OP. IMO if a conductor is not going to carry current at the same time as another conductor then the heat produced within a raceway would be the same as if the non carrying conductor were not there which is the intent of the deration to begin with. I can see some arguement to this but if there would be some type of interlock to keep both loads from operating at the same time then why not? A similar situation exists for feeder and service calculations as well as neutrals carrying unbalanced current. The real question is what are current carrying conductors for this particular situation?
I agree with Bobs logic but fact is NEC did not make an exception. Stupid as it is we must count it as 2. NEC says nothing about how often it is used. It is there to do what ? Carry current is its intent and it will. Not saying i think its right.
Code referance that permits this ?
____________________________6-50 Log #1405 NEC-P06 Final Action: Reject
(310.15(B)(2)(a), Exception No. 6 (New))
Submitter: George Stolz, II, Pierce, CO
Recommendation: Add an Exception to read:
Exception No. 6: Of those conductors that are switched cable or raceway
installations, only the maximum number of conductors capable of being
simultaneously energized need to be derated.
Substantiation: In most threeway and fourway switching methods, the load is
alternated between travelers, eliminating the need to include both travelers in
derating.
Panel Meeting Action: Reject
Panel Statement: The proposed exception is not necessary. The present
language of 310.15(B)(2) already permits what the submitter is proposing.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11