Can you mix 120 volt circuit with 4-20 Milliamp signal wiring? I need to run a race way up to water level reading that has 120 volt magnets that give level reading and a 4-20 Milliamp input. I would like to just use one raceway. The 4-20 cable in shielded. From what I was told you don't have noise issues with 4-20 ma signal wiring.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Can you mix 120 volt circuit with 4-20 Milliamp signal wiring? I need to run a race way up to water level reading that has 120 volt magnets that give level reading and a 4-20 Milliamp input. I would like to just use one raceway. The 4-20 cable in shielded. From what I was told you don't have noise issues with 4-20 ma signal wiring.

Look at 300.3(C)
 
The way to determine if they are Class 2 or Class 3 is to see what source supplies the conductors. Class 2 or Class 3 are listed and labeled as such. Maybe the designer of the system knows.

Don't forget about the insulation values required if the system supply is not Class 2 or 3.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
So, Pierre, do you know what determines if it is class 2 or class 3. Is there something in the design of the tranys or something like that?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
So, Pierre, do you know what determines if it is class 2 or class 3. Is there something in the design of the tranys or something like that?

Dennis,

Take a look at Chapter 9 Table 11(A) and 11(B) to see the difference in power limitations for Class 2 and Class 3 power supplys.

Chris
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Can you mix 120 volt circuit with 4-20 Milliamp signal wiring? I need to run a race way up to water level reading that has 120 volt magnets that give level reading and a 4-20 Milliamp input. I would like to just use one raceway. The 4-20 cable in shielded. From what I was told you don't have noise issues with 4-20 ma signal wiring.

My guess would be that the 4-20 Milliamp input would be either a Class 2 or 3 circuit and not permitted to be installed in the same raceway with a 120 volt circuit.

You may want to look at 725.130(A) Exception #2.