Well, we normally assume 75C wire so I am guessing you are not using 75C. Is this correct?i forgot to mention that i am coming from a meter/disco outside and hitting a panel about 50 ft away.Looking at table 310.16;for copper-4/0 and for aluminum 300's.
Dennis, i plan on using conductors rated for 75c...looking at table 310.16;i am looking at 3/0-copper and aluminum 250's.Am i missing anything?
Thanks Dennis,i appreciate your help.I have only been confused because the local inspector told me i could not use 4/0 al in a commercial building.I plan on doing a load calc to prove to him that i can indeed use the 4/0 al xhhw.
Seriously, why do you say that?You guys can be tough on a novice.
You are welcome
I don't understand the thinking about commercial vs residential. He is thinking this because of Table 310.15(B)(6) which allows 4/0 alum for resi. The problem is he is not looking at 240.4(B).
Now if you want a true 200 amp service -- a service capable of 200 amps, then you would have to use 250Kcm aluminum.
You guys can be tough on a novice.
You guys can be tough on a novice.
Trevor, I am one of those who believes T310.15(B)(6) supercedes art. 338. The Tables allow se cable in the heading so I think it is good if it carries the entire load of the dwelling. Now do I think it may have been overlooked--- Yes but as it reads I say SE cable is okay.What if he's using SE cable?