Thanks Dennis,i appreciate your help.I have only been confused because the local inspector told me i could not use 4/0 al in a commercial building.I plan on doing a load calc to prove to him that i can indeed use the 4/0 al xhhw.
I dont mean to rain on your party but.... You may need to check to see if there is a local amendment prohibiting alum. in commercial buildings also check the plans. The engineer may have specked copper if so you are bound to follow the specks unless you get a signed and stamped letter from the engineer stating that alum. would be acceptable. Or..... the inspector is mistaken. Then ask him to show you where it is in code.